Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Exterior Projections less than 4'

Status
Not open for further replies.
Jun 15, 2023
8
Possibly dumb question, but when NFPA 13 references exterior projections requiring fire sprinklers greater than 4' in width, are they referring to literal width or depth? I've always thought this as the distance the overhang projects away from the building, but maybe this is a massive oversight on my end?

 
Replies continue below

Recommended for you

The width is always the lesser of the two horizontal dimensions. The longer dimension is the length.

You could have a combustible projection extending 100' out from the building, but if the other dimension is 4' or less, no sprinklers required.

Similarly, you could have a combustible projection that runs 100' along the building, but if it only projects 4' or less out from the building, no sprinklers required.
 
Lol no worries. This forum is a ghost town compared to what it used to be, so it's nice to be able to take a stab at questions every now and again.
 
Yeah. There is not as much activity as we used to have. NFPA 13 in I believe the 2022 edition actually defined width just as noted above. It is the lesser of the 2 dimensions. Length is the greater.

Travis Mack, SET, RME-G,
MEPCad, Inc
AutoSPRINK | AutoSPRINK FAB | AutoSPRINK RVT

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor