I have external wall timber clad consists of 50mm cladding, 100 mm insulation, 10mm chipboard and 12.5mm plasterboard,140mm stud wall.
I manged to work out the loads as follow:
1- insulation load 0.1m x 0.5 density = 0.05 kN/m2
2- chipboard 0.01m x 7 density =0.07 kN/m2
3-Plasterboard 0.125m x 9 density = 0.1125 kN/m2
4- Timber wall Studs 0.5 KN/m2
However, I am not sure exactly how to work out the dead load of the 50mm cladding.
Normally, we take the total timber cladding wall as 1.35kN/m2. How can I justify this figure as the total load without 50mm cladding is 0.74, so is it correct to assume the 50mm cladding is 0.62 kN/m2.
Thanks
I have external wall timber clad consists of 50mm cladding, 100 mm insulation, 10mm chipboard and 12.5mm plasterboard,140mm stud wall.
I manged to work out the loads as follow:
1- insulation load 0.1m x 0.5 density = 0.05 kN/m2
2- chipboard 0.01m x 7 density =0.07 kN/m2
3-Plasterboard 0.125m x 9 density = 0.1125 kN/m2
4- Timber wall Studs 0.5 KN/m2
However, I am not sure exactly how to work out the dead load of the 50mm cladding.
Normally, we take the total timber cladding wall as 1.35kN/m2. How can I justify this figure as the total load without 50mm cladding is 0.74, so is it correct to assume the 50mm cladding is 0.62 kN/m2.