enigma2
- Feb 7, 2006
- 38
We have a project where we have been asked to come up with a solution to re-connect existing veneer to the structural back up of a 1928 structure. From what we can tell, the back up is a double wythe of clay tile and the veneer is a series of 4" thick solid concrete panels. The panels vary in size, the largest is about 20" x 12". A few of these panels are starting to pull away from the backup. It appears the worst one is sticking out about 1" from the rest of the wall. Removal of one of the loose pieces shows there is no grout between the clay tile and the concrete panel.
The mortar joints between the veneer pieces are very slight--1/8" to 3/16", so the use of a wall tie system seems implausible, since most of these retrofit ties are at least 1/4" in diameter. Plus, since the veneer is a harder substrate than the backup, we are concerned these ties will just get stripped and be ineffective by the time they are threaded in and make their way to the clay tile backup.
We are considering the use of an epoxy adhesive anchor with a screen tube countersunk into the concrete panel. We have some apprehensions that this solution may be a bit too rigid and ultimate introduce the potential for cracks in the concrete panel, but we're not sure what other options we have. We don't need to push these pieces back up against the clay tile, we just need to make sure they don't scoot out more and fall off the structure.
Is the epoxy adhesive anchor feasible? Any other ideas?