- May 28, 2022
- 29
When elevator contractors provide machine room loads to the structural engineer, these loads have been calculated by doubling the live loads (car, counterweight, etc) to account for impact. Should I be further factoring these loads or is this overly conservative?
One engineer I spoke with mentioned they don't further factor the loads because they are using ASD philosophy. IMO this still seems overly conservative via the omega factors used for ASD.
For reference, this broader question is coming up because I have come across a situation where a previous contractor used a channel in minor axis bending. It looked odd to me so I ran some quick numbers. The only way this passes LRFD or ASD is if I use the static load values instead of doubling for impact. When using the impact values, it fails ASD by 40%. This elevator has been in normal service like this for 10+ years, with no obvious signs of deflection on the channel in question.
Any insight here is greatly appreciated.
One engineer I spoke with mentioned they don't further factor the loads because they are using ASD philosophy. IMO this still seems overly conservative via the omega factors used for ASD.
For reference, this broader question is coming up because I have come across a situation where a previous contractor used a channel in minor axis bending. It looked odd to me so I ran some quick numbers. The only way this passes LRFD or ASD is if I use the static load values instead of doubling for impact. When using the impact values, it fails ASD by 40%. This elevator has been in normal service like this for 10+ years, with no obvious signs of deflection on the channel in question.
Any insight here is greatly appreciated.