eastendeng
Civil/Environmental
- Jun 30, 2008
- 11
I've got a large concrete parking lot pour. The concrete is supposed to be 4,000psi with fiber reinforcement and general specs in accordance with ACI 330.1-03. One slump test and one set of cylinders were taken for each 50yds. Cylinders had a 7 day ave of 2,160psi and 28 day ave of 3,355psi. the concrete supplier took their own QA samples and I'm trying to see their results for comparison. the subgrade compaction was confirmed within acceptable density and moisture limits. What is the acceptable mitigation? removal and replace? Wait for signs of failure then replace? combination?