TEDstruc
Civil/Environmental
- Dec 6, 2017
- 43
I'm looking for opinions on whether or not bolted tension members that see cyclic load can use snug tight bolts (bearing type connection). In this case, lets consider an angle tension hanger with a bolted connection (bolts in shear) that supports a piece of equipment that sees some cyclic load. The company I work for (an equipment manufacturer) installs thousands of hangers like this using a specified bolt installation torque. I've estimated that for non-PT bolts we are getting the bolt to about 50% of a fully pretensioned bolt (on a 3/4" bolt say 16 kips of pretension vs 28 kips for a fully pretensioned A325 bolt).
Most of the hangers installed are seeing relatively low cyclic load that would not exceed the fatigue threshold stress (Fth) that is specified in Table A-3.1, Section 2.3 (for rivets or snug-tightened bolts). However, in the commentary under section 3.4, it states that non-pretensioned fasteners are not permitted for joints subject to cyclic shear forces... If non-pretensioned bolts are not allowed in this application, why is section 2.3 included? Is it just to cover existing connections that aren't fully pretensioned?
Most of the hangers installed are seeing relatively low cyclic load that would not exceed the fatigue threshold stress (Fth) that is specified in Table A-3.1, Section 2.3 (for rivets or snug-tightened bolts). However, in the commentary under section 3.4, it states that non-pretensioned fasteners are not permitted for joints subject to cyclic shear forces... If non-pretensioned bolts are not allowed in this application, why is section 2.3 included? Is it just to cover existing connections that aren't fully pretensioned?