rockman7892
Electrical
- Apr 7, 2008
- 1,156
We recently had a fault on one of our 4.16kV motor starters that was pretty big in magnitude. It appeas the fault happend due to a loose bus connection where the starter section's vertical bus terminates on the contactor stabs. The attached picture shows a screw being missing most causing a loose connection on this bus, and as soon as motor was started fault occured. It is assumed that the loose connection was arcing, and somehow this arcing caused a L-L fault with one or both of the other phases.
I say a L-L fault because looking at my upstream relays it shows what appears to be a phase fault of aprox 22kA. Our upstream breaker actually tripped on a ground fault but the phase overcurrent element picked up when the 22kA or so was seen. I guess somehow this L-L fault produced some ground current as well.
Our system is a 4.16kV primary distribution system which is LRG to 400A at the utility substation.
I have the event reports/waveforms from both my main breaker (multilin 750) and the utility's 387E schweitzer relay. The 387E relay is monitoring the utility transformer differential with winding 1 being the primary side, and winding 2 being the secondary side. Winding 3 is looking at the transformer tank ground connection.
The utility says that they saw the same 22kA current magnitude on the secondary but claim they saw about 2000A on this tank ground CT. I question how they can see this magnitude of ground current if we are resistance grouned limiting current to 400A? Can this current get above 400A?
I'm by no means an expert at interpreting these event reports, and wanted to see if anyone was interested in looking at these event reports to see what appears to be the sequence of events and analysis of the fault. I am interested to learn from others input. I also do not have the correct software to view utilites relay files.
I will attached multilin 750, and schweitzer 387E relay in following posts.
Thanks for the help.
I say a L-L fault because looking at my upstream relays it shows what appears to be a phase fault of aprox 22kA. Our upstream breaker actually tripped on a ground fault but the phase overcurrent element picked up when the 22kA or so was seen. I guess somehow this L-L fault produced some ground current as well.
Our system is a 4.16kV primary distribution system which is LRG to 400A at the utility substation.
I have the event reports/waveforms from both my main breaker (multilin 750) and the utility's 387E schweitzer relay. The 387E relay is monitoring the utility transformer differential with winding 1 being the primary side, and winding 2 being the secondary side. Winding 3 is looking at the transformer tank ground connection.
The utility says that they saw the same 22kA current magnitude on the secondary but claim they saw about 2000A on this tank ground CT. I question how they can see this magnitude of ground current if we are resistance grouned limiting current to 400A? Can this current get above 400A?
I'm by no means an expert at interpreting these event reports, and wanted to see if anyone was interested in looking at these event reports to see what appears to be the sequence of events and analysis of the fault. I am interested to learn from others input. I also do not have the correct software to view utilites relay files.
I will attached multilin 750, and schweitzer 387E relay in following posts.
Thanks for the help.