FernandoCFE
Electrical
- Aug 5, 2003
- 15
I have the next situation:
In a substation (115 kV system) I found a fault level of 43 kA (symmetrical value) in the busbar, and the switchgears in this substation are 40 kA (symmetrical).
The 43 kA are the result of a vectorial sum of the contributions of the derived circuits conected to this substation, but in a fault after a switchgear, the fault current that will flow through this switchgear will be less than the total fault current in the busbar and less than 40 kA.
Can I assume that this switchgear will withstand the fault?
Any reference about this issue, will be appreciate!
FernandoM
In a substation (115 kV system) I found a fault level of 43 kA (symmetrical value) in the busbar, and the switchgears in this substation are 40 kA (symmetrical).
The 43 kA are the result of a vectorial sum of the contributions of the derived circuits conected to this substation, but in a fault after a switchgear, the fault current that will flow through this switchgear will be less than the total fault current in the busbar and less than 40 kA.
Can I assume that this switchgear will withstand the fault?
Any reference about this issue, will be appreciate!
FernandoM