Non fused HP rated disconnect switches (at motors) are mostly rated 10,000 amps at 480 volts. Assume there is NOT an interlock (micro switch back to the contactor) to make sure that the contactor is dropped out when the switch is open, there is a slim chance the HP rated switch can be closed into a fault if the contactor is picked up.
Assuming the fault current is greater than 10,000 amps at the switch, then this is a bad application?
Based on what I see of designs, this is seldom reviewed, considered, or looked at.
Am I being too careful and detailed or am I missing somethig?
Opinions Please
Thanks
JIM
Assuming the fault current is greater than 10,000 amps at the switch, then this is a bad application?
Based on what I see of designs, this is seldom reviewed, considered, or looked at.
Am I being too careful and detailed or am I missing somethig?
Opinions Please
Thanks
JIM