Hi all,

I am wondering for a generator of fixed rating, does an induction generator or synchronous generator have better fault ride through capability.

I imagine it would rely quite heavily on the inertia of the rotor. So which topology has a the highest inertia rotor. Also a synch genny will rotate slightly slower.

I guess this leads onto another question, for equal rating will a synch generator or induction generator be heavier/bigger. I would guess a synch generator would be smaller as I imagine the airgap flux density would be larger than that of an induction generator due to excitation rather than induction (all things being equal).
 
Replies continue below

Recommended for you

Suggestion: Normally, it is prudent to trip a generator on the fault. Is this a theoretical question? When it comes to a heavy load transient, then it would depend on the rotating mass inertia.
 
I'm not clear what you mean by "fault ride-through" as applied to a generator.
 
When I say fault ride through I mean the ability of a sync generator to remain in synchronism with the grid when there is a network fault that is cleared.

Refering to the swing equations it seems that rotor inertia is the main factor. Assuming this is true which topology would have a rotor of greater inertia.

What I don't understand and have't been able to find any literature on is fault ride through (or the equivalent of) for an induction generator. I realise there isn't a syncronisation issue but there must be the concern of motoring/reverse power or large current transients or reactive power issues?
 
I don't think loss-of-synch is generally a problem for synch machines during a fault. The concern is heating due to high current demand.

For an induction generator, you will generally lose your excitation since the bus voltage will go near zero, so I would not expect them to help you much. If you tried to keep them on line, the speed may go high.

But I'm not burdened by a lot of actual knowledge about induction machines, so it's easy to speculate.
 