cdafd
Specifier/Regulator
- Aug 18, 2005
- 2,937
Say I have two buildings on the same lot, say 20 feet apart.
Both have separate wet risers in them.
Owner decides to join the two buildings and make one.
So the fire sprinkler system is extended from one of the existing risers.
Per NFPA 13, is it legal,:::::::::
1. To connect the two together, in order to eliminate one fdc.
2. Put a check valve in the connection, so neither riser is over the sq ft limit.
3. The interconnection would be from each of the systems largest pipe.
4. The FDC would be on the system, with the check flowing into the other system.