Hi
Does any one have some guidance/standards on the criteria of relay settings for distribution feeder protection (27.6kV and below), espacially for those breakers that do not have reclose function and the feeder protection relay does not have both low-set inst. and the hi-set inst.? My concern is how much percent in terms of the total feeder length that the inst. overcurrent pick-up setting should cover, do you want inst. overcurrent to see the end of line fault or you want it only to see the fault at the first tapping pole and the rest will trip on time delayed overcurrent? I think that is a trade-off between fuse-saving and the reduction of SAIDI and SAIFI, but I don't have clear mind on the criteria, so I appreciate any helpful thought!
Thanks in advance?
Does any one have some guidance/standards on the criteria of relay settings for distribution feeder protection (27.6kV and below), espacially for those breakers that do not have reclose function and the feeder protection relay does not have both low-set inst. and the hi-set inst.? My concern is how much percent in terms of the total feeder length that the inst. overcurrent pick-up setting should cover, do you want inst. overcurrent to see the end of line fault or you want it only to see the fault at the first tapping pole and the rest will trip on time delayed overcurrent? I think that is a trade-off between fuse-saving and the reduction of SAIDI and SAIFI, but I don't have clear mind on the criteria, so I appreciate any helpful thought!