Hello,
In article 215.2(A) the code says a feeder has to be size by either (1) 125% of the continuous load plus the non-continuous load OR (2) ampacity adjustment after load correction factors. This implies that if I have a commercial installation and after adjustments I end up with 310A, that I can use a feeder size of #350 MCM at 75C.
However, in 215.3, the feeder overcurrent protection requirements seem to override 215.2(A)(2). It states that if the feeder supplies continuous loads or any combination of continuous and non-continuous loads, then the feeder overcurrent protection has to be sized at 125% of the continuous load plus the non-continuous load, and of course the feeder ampacity needs to be at least as large as that.
Am I mistaken or does 215.3 completely nullify 215.2(A)(2)?
Thanks
In article 215.2(A) the code says a feeder has to be size by either (1) 125% of the continuous load plus the non-continuous load OR (2) ampacity adjustment after load correction factors. This implies that if I have a commercial installation and after adjustments I end up with 310A, that I can use a feeder size of #350 MCM at 75C.
However, in 215.3, the feeder overcurrent protection requirements seem to override 215.2(A)(2). It states that if the feeder supplies continuous loads or any combination of continuous and non-continuous loads, then the feeder overcurrent protection has to be sized at 125% of the continuous load plus the non-continuous load, and of course the feeder ampacity needs to be at least as large as that.