kobedog
Civil/Environmental
- Jan 12, 2003
- 3
I have a contractor that due to lot line problems wants to install fence posts directly into the center part of a Vertica pro (anchor wall) segmental retaining wall. When I calculate the overturning forces from the wind load (assume 6' tall posts' 8 feet apart, then use UBC to get coefficients)my driving moment exceeds the resisting moment. The driving moment from the wind load I calculate is 2 k lb-ft/ft and the resisting moment is only the first 4 layers of block solid grouted 4 x140 - 560 lb-ft/ft. The only way to really get it to work is to add a large concrete strip behind the wall to get extra overturning moment resistance. I have seen some contractor install the fences into block walls without adding the extra concrete and they seem to be holding fine. Am I over-calculating the driving moment form the wind load - or are some other contractors just cutting corners. Thanks in advance for the help.