OhioAviator
Electrical
- Sep 8, 2003
- 123
I have an existing facility that was built 30+ years ago where the 480V power is supplied by transformers with ungrounded delta secondaries. As such, no equipment grounding conductors were pulled through the conduits between the ungrounded delta transformer secondaries and the motor control centers, or between the motor control centers and the individual motors out in the plant. Instead, the rigid steel conduits are used as the equipment grounding conductors, which the NEC does allow. The vast majority of the conduit runs between the motor control centers and the motors are buried in underground duct banks. I am concerned about corrosion over time that may have occurred with the buried rigid steel conduits and do not have high confidence that the existing buried conduits are actually capable of carrying the likely fault currents that could develop in the event of a double phase to ground fault. In my mind, it isn't adequate to simply conduct a ground resistance test between each motor and the motor control centers. Even though that test does measure the resistance of the ground return path, it doesn't measure how much current the 'equipment grounding conductor' (the steel conduit in this case) can actually carry during a fault without failure of a corroded conduit joint or the conduit itself. Does anyone know of a test that can be performed on buried rigid steel conduit to determine its fault current carrying ability, and hence it's suitability to continue to be used as an equipment grounding conductor? Am I worried over nothing?
Thanks in advance for your help.
Galatians 2:20
Thanks in advance for your help.
Galatians 2:20