I have a structure that I recently designed and is currently under construction. The building is a medical office and was designed using the IBC 2009 with a floor live load of 80psf (we use 80 vs 50 (live) + 20 (par)). There is now a tenant who would like to have a file storage room added to their layout (this after we specifically discussed file storage in meetings and how it wasn't needed). My question is how to figure out if the file storage overloads the floor.
If you figure the actual load of a cabinet on the floor we are talking about 200psf which is nowhere close to working. However, if you add up the total weight of the storage area and then divide it by the floor area it takes up you are looking at a load of 40psf. Now this doesn't figure for any LL around the cabinets which would need to be added.... say at 50psf. Floor construction consists of steel joists at roughly 2'-6" o.c.
How do others figure the effects of file storage on their floors?
If you figure the actual load of a cabinet on the floor we are talking about 200psf which is nowhere close to working. However, if you add up the total weight of the storage area and then divide it by the floor area it takes up you are looking at a load of 40psf. Now this doesn't figure for any LL around the cabinets which would need to be added.... say at 50psf. Floor construction consists of steel joists at roughly 2'-6" o.c.