Finite Element Modeling of underground junction box, for storm drainage, with holes for pipes
Spellbinder
6
I am modeling a junction box for storm drainage in RISA3d. Its an underground concrete box with some hols for pipes.
When i model the box with circular or rectangular cutout for pipes the shear concentrates a lot, which seems unrealistic. I need ideas or reference, that will help me reduce this shear.
Please let me know if you need more information
For stress concentrations, a good reference 'Roark's Formulas for Stress and Strain'.
In situations where a homogeneous, ductile material is subjected to loads that will not create fatigue.....stress concentrations are generally ignored. (But that probably wouldn't work for RC.)
Warose,
Where in roaks book can I find stress concentration can be ignores?
Warose,
I don't think it comes out and says it anywhere. I was referring to a industry practice with a ductile material (like A36 steel) not subjected to cyclic loads.
The hard part is (of course) knowing if the stress is indeed a concentration and how widespread it is. That's where a reference like Roark's comes into play.
With something like reinforced concrete.....that's a different ballgame. It's hard to give a one-size-fits-all solution there......but you can (for example) average the effects for highly concentrated forces/stresses.
I have uploaded 2 files. the loaing is the soil pressure from outside.
one showing the shear for my model. this boxes without any hole has a highest shear of 14.5 kips per ft. But with the holes the shear goes as high as 31 kip per ft.
I have another file showing where the shear is higher than 14.5 kips per feet. Hopefully that will give a better picture of what i am talking about.
Thanks for the replies. Hope to get a better understanding of whats going on from the discussion.
This is a modeling issue. I am not familiar with RISA3d but you should try refining your mesh and check how you are applying the loading especially around the openings. The most common/simplest method of resolving this is to average the shear stress of several elements in an area. This will give a more realistic idea of the shear stress.
From a design perspective, I try to put develop a bar at areas where you see stress concentrations. This reduces the chance of cracking at that area.
Select only the section you're checking for shear and use the section cut feature of RISA 3D. This will give you much more realistic forces in a unit width of plates.
Ian Riley, PE, SE
Professional Engineer (ME, NH, VT, CT, MA, FL) Structural Engineer (IL, HI)