Fire Alarms Testing and Inspections Requirements

Status
Not open for further replies.

NJ1

Mechanical
Feb 9, 2010
381
0
0
US
I would like a little guidance from the experts here. I am not too familiar with fire alarms but I would like to start preparing for my first NICET test in alarms ever.

I know that it is not the intent of the NFPA 25 to identify installations flaws. My questions is: Does the same philosophy applies to NFPA 72
 
Replies continue below

Recommended for you

Does anyone use the maintenance regimes in NFPA 72? They seems very ownerous. All detectors to be individually tested over a 5 year interval and you need record which detectors have been tested, keep this record for 5 years and make sure you test all of them, then start again.

Do testing contractors do all this?
 
Assuming your are refering to the requirement to perform a sensitivity test on smokes, we do. The state FMs we work with allow us to do 20% per year. I have decided less than 20 smokes, we test all of smokes every 5 years and over 20 smokes, we test 20% per year.
 