fire fighting pump performance test 1

Status
Not open for further replies.

mirghaffari

Mechanical
Dec 24, 2012
54
Dear all,

Thanks for your always support,
could you please introduce a standard for testing the performance of the fire fighting pump?i could not find performance test tolerance values in NFPA 20.

Thanks for your help
 
Replies continue below

Recommended for you

Perhaps Hydraulic Institute testing standards would be applicable. Not sure of the size of your pump, but this is the place I would start.

 
That's part of the problem about the NFPA that it doesn't really address pump issues. I'd go for duty points and no more than 10% away from values.

My motto: Learn something new every day

Also: There's usually a good reason why everyone does it that way
 

Check out UL and FM requirement for the fire pump listing. Most likely follow HI standard.
 

Thanks every one for your help
After your guidline i found it in HI standard.

Dear pumpsonly,
Your answers are always helpfull.
Thanks again
 