So, to my first question: What do your calculations tell you? Have you done calculations? At least a preliminary set? You don't give the slope. Is it >2:12? Is it ≥4:12?
What is your attic structure spacing? These are all required to determine the answers to your questions. Do you have a lot of experience in fire sprinklers? Are you looking to confirm your answer, or are you looking to take a $50k gamble on a response from an internet forum?
Depending on how you design your attic, you could have a demand around 500 gpm with a dry system and sloped attic. Assuming you have ±45 psi at system demand, you need to deduct the following approximations:
Elevation pressure: ±9 psi
End sprinkler pressure: 7 psi
10% safety margin: ±5 psi - I would probably take this to 10 psi.
Backflow preventer losses: ±5 psi
This leaves you with ±14-19 psi for friction loss in a dry system. Are you willing to gamble that you can do a dry system with less than ±14-19 psi in friction losses? I have no idea what your building looks like to know if that is even possible. You may want to seek help of someone that you compensate for their time, skills and opinion to assist you with this.
Travis Mack, SET, CWBSP, RME-G, CFPS
MFP Design, LLC