Good day,
I am checking the fire drawings of a project, The fire pump is sized to be 1500 gpm, but as per NFPA 14 section 7.10.1.1.5 "The maximum flow rate shall be 1000 gpm (3785 L/min) for buildings that are sprinklered throughout, in accordance with NFPA13, Standard for the Installation of Sprinkler Systems, and 1250 gpm (4731 L/min) for buildings that are not sprinklered throughout, in accordance with NFPA 13." my project is fully sprinklered so I proposed to change the pump to 1000 gpm. But he designer claims that additional 500 gpm is needed for external fire hydrants.
My question is there anything in NFPA that say I need to consider for internal and external fire at the same time and if possible to point which sections talk about this issue?
I am checking the fire drawings of a project, The fire pump is sized to be 1500 gpm, but as per NFPA 14 section 7.10.1.1.5 "The maximum flow rate shall be 1000 gpm (3785 L/min) for buildings that are sprinklered throughout, in accordance with NFPA13, Standard for the Installation of Sprinkler Systems, and 1250 gpm (4731 L/min) for buildings that are not sprinklered throughout, in accordance with NFPA 13." my project is fully sprinklered so I proposed to change the pump to 1000 gpm. But he designer claims that additional 500 gpm is needed for external fire hydrants.