jjmoore73
Mechanical
- Apr 13, 2011
- 30
When determining maximum static suction pressure, we are provided a maximum static by the water authority, based upon elevation at public Point of Connection and 0 GPM flowing through the public network. The provided pressure will not exceed this at POC and very likely will not achieve the maximum pressure since water is always flowing through the public network.
The private property has a reduced pressure backflow device to protect the public supply. The private side will have less pressure than the public side due to the reduced pressure backflow device. It would make sense the reduction in pressure from the RP backflow along with elevation adjustment could be used when determining the maximum static pressure at the pump suction flange.
If I was to test the private onsite hydrant for static pressure, it would include the RP backflow pressure loss, and we would then only adjust for elevation.
Thoughts?
4.7.7.1 The net pump shutoff (churn) pressure plus the maximum
static suction pressure, adjusted for elevation, shall not
exceed the pressure for which the system components are
rated.
The private property has a reduced pressure backflow device to protect the public supply. The private side will have less pressure than the public side due to the reduced pressure backflow device. It would make sense the reduction in pressure from the RP backflow along with elevation adjustment could be used when determining the maximum static pressure at the pump suction flange.
If I was to test the private onsite hydrant for static pressure, it would include the RP backflow pressure loss, and we would then only adjust for elevation.
Thoughts?
4.7.7.1 The net pump shutoff (churn) pressure plus the maximum
static suction pressure, adjusted for elevation, shall not
exceed the pressure for which the system components are
rated.