Hi,
I'm trying to select a packaged diesel fire pump to provide flow to a hydrant on a site. The facility is connected to the city's fire water line, but does not have enough pressure. If a fire hydrant is required to have 1500 gpm at 20 psig, does one select a pump for 1000 gpm or 1500 gpm?
I think NFPA 20 mentions something about the fire pump being able to handle 150% of its rated capacity. Can I say that my pump "rated capacity" is 1000 gpm, and therefore, 150% of my rated capacity is 1500 gpm, and would meet the fire hydrant flow requirement? Or do I select a pump for 1500 gpm + 50% = 2250 gpm?
If the facility has a fire hydrant (1500 gpm) and 2 buildings (bldg A: 225 gpm and bldg B: 300 gpm) that require fire sprinkler system. Does one size the fire pump for a fire hydrant + bldg B = 1800 gpm, or just the worst case (1500 gpm)?
Thanks.
I'm trying to select a packaged diesel fire pump to provide flow to a hydrant on a site. The facility is connected to the city's fire water line, but does not have enough pressure. If a fire hydrant is required to have 1500 gpm at 20 psig, does one select a pump for 1000 gpm or 1500 gpm?
I think NFPA 20 mentions something about the fire pump being able to handle 150% of its rated capacity. Can I say that my pump "rated capacity" is 1000 gpm, and therefore, 150% of my rated capacity is 1500 gpm, and would meet the fire hydrant flow requirement? Or do I select a pump for 1500 gpm + 50% = 2250 gpm?