Dormer1975
Mechanical
- Aug 31, 2007
- 25
As we all know, fire departments/jurisdictions use a specific gallonage requirement (i.e. 4,000gpm in my example) @ 20 psi as their requisite fire flow. How do I size a fire pump @ 20 psi? In my experience, pump curves don't go that low. I don't do a lot of pumps, maybe 1-2 a year, but most of them are sized by the sprinkler system demand and less by fire flow (they are storage facilities with large sprinkler systems). I understand why fire departments use this nomenclature. They are going to show up to fight a fire and they will hook up to a hydrant with their trucks, that have pumps on them, and they want to know that they have sufficient pressure to not create vacuum and also enough water (gpm) to supply their trucks' pumps. If I spec a 3,000 gpm @125 psi pump, that's its rating. At 150% of rated flow it will provide 4,500 gpm @ typically 60% of rated pressure (75 psi in this example) (varies by manufacturer). But, the curve doesn't keep going to represent flow @ 20 psi. The manufacturer says 3,750 gpm...that's all you're going to get...but it's at 75 psi (in this example). Any suggestions or experience with this? I'm scouring NFPA 20 to see if they have recommendations as well.