Vusal Quliyev
Mechanical
- Dec 4, 2018
- 26
Dear Experts,
There is confusing topic about NFPA 14 and NFPA 20 to discuss with you:
If we have Fire Pump serving to header and this header serves to Class I stand pipe system, Class II stand Pipe System and Sprinkler system. (3 pipe coming from pump room). Can we consider this system as combined system or not? (I need to know if we can omit the GPM coming from sprinkler system as stated - 7.10.1.3.1.2 A separate sprinkler demand shall not be required.)
If not, how should we calculate total required Fire Pump GPM? Is it right to calculate like: 500 GPM (from Class I - 14:7.10.1.1.1) + 100 GPM from (Class II - 14:7.10.2.1.1) + Sprinkler Flow Rate (hydraulic calculation)
Your opinion is important.
There is confusing topic about NFPA 14 and NFPA 20 to discuss with you:
If we have Fire Pump serving to header and this header serves to Class I stand pipe system, Class II stand Pipe System and Sprinkler system. (3 pipe coming from pump room). Can we consider this system as combined system or not? (I need to know if we can omit the GPM coming from sprinkler system as stated - 7.10.1.3.1.2 A separate sprinkler demand shall not be required.)
If not, how should we calculate total required Fire Pump GPM? Is it right to calculate like: 500 GPM (from Class I - 14:7.10.1.1.1) + 100 GPM from (Class II - 14:7.10.2.1.1) + Sprinkler Flow Rate (hydraulic calculation)
Your opinion is important.