Rolland1
Mechanical
- Aug 4, 2010
- 2
NFPA 20-2007 allows the designer to hydraulically size the pipe for the test header art. 4.20.3.4(2).
There's no mention of the acceptable pressure. Figure 4.20.3.4.(2) identifies the elements that must be included in the calculation, but there's no design critereas.
Should I consider that the acceptable pressure drop is the residual pressure of the water source at a flow of 150% the nominal pump flow?
Thanks
There's no mention of the acceptable pressure. Figure 4.20.3.4.(2) identifies the elements that must be included in the calculation, but there's no design critereas.
Should I consider that the acceptable pressure drop is the residual pressure of the water source at a flow of 150% the nominal pump flow?
Thanks