Dave,
I agree with your assesment with regards to an inspector's responsibilities while performing an annual performance test on a fire pump or any fire sprinkler devices for that matter.
NFPA 25HB 2010 states:
The contract with a fire protection contractor to perform the inspection, testing, and maintenance of a waterbased fire protection system is not an insurance policy or an engineering evaluation. If the property owner is ever uncertain whether the fire protection system as installed will provide the minimum protection required by the applicable codes, the owner should contact a fire protection engineer or qualified contractor to perform an analysis of the building, the building occupancy, the commodity classification of any storage present, the system design criteria, and the water supply.
The inspection and testing of a fire protection system in accordance with NFPA 25 is not equivalent to any of the following:
1. An engineering or AHJ review or evaluation of the
adequacy of the system to control or extinguish a fire
in the protected occupancy
2. An engineering or AHJ review or evaluation of the
adequacy of the water supply, including water tanks
and fire pumps, to provide the necessary waterflow
and pressure needed to meet the fire protection system
demand as designed
3. An engineering or AHJ review or evaluation of the
hazards present in the facility to determine the required
system criteria for minimum protection levels
4. An engineering or AHJ review, evaluation, acceptance,
inspection, or test of the fire protection system to determine
whether the system was designed and installed in
accordance with the applicable installation standard,
including NFPA 13, 13R, 14, 15, 16, 20, 22, and 214
5. An engineering or AHJ review or evaluation of all
areas of the facilities to determine whether all areas of
the facility are protected in accordance with the original
applicable installation standard
The NFPA Technical Committee on Inspection, Testing, and Maintenance of Water-Based Systems has made it clear that the role of the inspector performing inspection and testing activities in accordance with NFPA 25 is not that of a fire protection engineer or an AHJ. The inspector is not required to be a fire protection engineer, nor is the inspector required to have detailed knowledge of the fire protection system installation requirements in the applicable NFPA standards. Therefore, when property owners contract with a fire protection contractor, they should not expect the inspector to provide an engineering analysis detailing the adequacy of the system design when compared to the hazard, or evaluate the accuracy and completeness of the installation.
The inspector is not required to perform the following
functions:
? Review the design criteria for the system to determine
whether it is adequate for the commodity or hazard
? Review the installation shop drawing to make sure all
pipes are correctly sized and the sprinklers are the correct
type, orifice size, and temperature rating
? Perform a water supply analysis to determine whether
the water supply is sufficient to provide the required
gallons per minute at the required pounds per square
inch for the system
? Perform a complete building inspection to determine
whether closets, blind spaces, attics, crawl spaces, and
all other special building features are adequately protected
in accordance with the version of the installation
standard in force at the time of the installation
? Recognize that storage commodities and/or arrangements
are different from those anticipated when the
system was designed and installed
? Research the installation contract files to determine
whether special requirements were required by the AHJ
See item 2 under equivalencies above!!
Thanks
Jamey