AdamMurray

Mechanical
Dec 23, 2003
18
0
0
CA
We have building with several double interlock preaction systems all served by one common riser. This system is boosted by an electric fire pump complete with a pressure relief valve set at 170 psi.
The problem we are having is to do with system overpressure at pump start up. When the pump starts it provides a "bump" on the system raising the system pressure above the check valve to approx. 245 psi. Conversations with relif valve manufacturers indicate that these valves do take a second or two to open.

My question is: How can we contain the initial bump without modifying the pump. My initial thoughts are some type of retard chamber, however I am not familiar with these with such a pressure bump. Any ideas?
 
Replies continue below

Recommended for you

First, find the engineer who designed this and slap him for over-sizing the pump then quick-fixing it with a pressure relief valve. NFPA 20 is quite clear that this practice is not acceptable.

There are surge suppressers available for this type of application. I don't know of a mfg off hand, but I do have a picture of one and will be glad to send it to you. Let me know.
 
A late post, but the two manufactures I know of are Greer and Young Engineering. These companies have UL listed equipment. They are very pricey. Other companies make ASTM compliant tanks.

I agree with Scott, the original designer screwed up big time. I recently worked on a project very similar. The only solution other than replacing the pump that I know of is to add a pressure-reducing valve. I personally think it is a poor solution but have seen other people use them. Then in addition to the pressure-reducing valve they installed a couple surge tanks.

Good Luck.
 
Hi,

I heard they sometimes solve this problem wit a jaw-way valve (don't know if I spell it correctly) . This is a valve with a quick response time, to relief the pressure in the system.

This bump could also be the result of water hammering. Check literature how to prevent this from hapening.

bye
 
What pressures does the fire pump come on and what pressure does the jockey pump come on at? If the fire pump is coming on at a too low pressure, it will cause a water hammer. NFPA 20, 2003 sectionA14.2.7 indicated a 10 psi difference between the jockey start and fire pump. I see many pumps where the difference is sometimes 100 psi ( client does not want the fire pump to come on!). I have also have found pumps were the set point for the fire pump is below the incoming city pressure. This is not good either.
 