jrfroe
Structural
- May 30, 2002
- 50
I'm working on an 1800 square foot single story CMU addition to an existing building. Since the existing building (built in the 1950's) is over the allowable height per IBC Table 503 (2009 IBC) for the construction type, we need a double fire wall that can't be tied to the existing building (per IBC 706.2). The existing building wall will provide the fire rating for one side of the wall, and the new building wall will provide the fire rating for the new building. This isn't a problem for walls above the foundation, but the city plan examiner is insisting that the separation has to extend through the foundation. The existing building is supported on steel piles with pile caps that extend approximately 6' into the space to be occupied by the new building. The new addition will be supported on micropiles, and is adjacent to the existing building on the south and west sides. The problem I'm having is that the southwest corner of the new building is over an existing pile cap and I don't think it is reasonable to not support the corner of the new building off of the existing pile cap, as I would need to design a fairly significant cantilevered grade beam that extends over the cap, and I'd be concerned with CMU wall cracking due to deflection of the cantilever. The existing pile cap supports a 12 story column, and I'm not adding enough load to overstress the existing foundation.
Does anyone know if there is something I'm missing in IBC that would prohibit having a common foundation between two sides of a double fire wall?
Does anyone know if there is something I'm missing in IBC that would prohibit having a common foundation between two sides of a double fire wall?