We are working on a project which requires retrofitting to bring the building up to code.
This is a reinforced concrete and CMU building constructed by the U.S. Navy and consists of reinforced concrete footings, floor slab, columns, beams and roof. The walls are reinforced 8" CMU.
One of the issues for the retrofit is that we need to separate the 15,000 SF building into two "fire building" one consisting of 10,000 SF and the other 5,000 SF to qualify under the 12,000 SF max floor space allowed before sprinklers are required.
So here's the issue: The architect insists that the fire wall should penetrate both the 8" floor slab and the roof slab. Our position is that with the exceptions for continuity provided in IBC 706.5 and 706.6 the fire wall (6" CMU) can be placed directly on the floor slab and flush up against the roof slab.
Our opinion is that the exceptions apply in this case - the architect disagrees. The Fire Marshall says he is with me as long as I am willing to certify that it is a fire wall and not a fire-resistant wall.
Any one out there run across this issue before?
Thanks.
This is a reinforced concrete and CMU building constructed by the U.S. Navy and consists of reinforced concrete footings, floor slab, columns, beams and roof. The walls are reinforced 8" CMU.
One of the issues for the retrofit is that we need to separate the 15,000 SF building into two "fire building" one consisting of 10,000 SF and the other 5,000 SF to qualify under the 12,000 SF max floor space allowed before sprinklers are required.
So here's the issue: The architect insists that the fire wall should penetrate both the 8" floor slab and the roof slab. Our position is that with the exceptions for continuity provided in IBC 706.5 and 706.6 the fire wall (6" CMU) can be placed directly on the floor slab and flush up against the roof slab.
Our opinion is that the exceptions apply in this case - the architect disagrees. The Fire Marshall says he is with me as long as I am willing to certify that it is a fire wall and not a fire-resistant wall.
Any one out there run across this issue before?
Thanks.