If it is just simply an office building with ceilings <10', metal building and no storage, wet pipe system & quick response sprinklers, the flow could be as low as 100 gpm interior demand and a hose allowance of 100 gpm.
If you have a wood structure with slopes >=4:12, you could have a demand of 500+ gpm interior and 100 gpm hose allowance.
The pressures could be as low as 25 psi at the base of the riser for the wet system and around 50 psi at the base of the riser for the dry system. All of the pressures can be modified with pipe sizing.
So, as you can see, more information is needed to get what you want.