Fire Water Ring Minimum Diameter 1

Status
Not open for further replies.

Engr. Mohammad

Mechanical
May 29, 2023
5
Dear colleuges,

Is there any code mandate the minimum size of the fire water main ring?
If yes, Please share with me that reference.
 
Replies continue below

Recommended for you

What are your local rules for fire water piping?
These rules are common and they have guidelines in them.


= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, consulting work welcomed
 
Don't think it's in any code as there are too many variables, but I've rarely seen one less than 4".

Look in the NFPA regs?


Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
Depends on flowrate and length.

It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)
 
Appreciate all responses from your side. in the local codes there is no specific requiremnets to it. and NFPA-24 specify it should based on hydraulic claultions, or 6 inch minimum if feeds hydrants, etc.
for that i asked may be there is any other sections in NFPA mentioned this point.
 
The is a specific NFPA forum under Engineering codes.

Try a search in that forum or ask the same question there but link to this one as well.

But if you have a facility that needs a ring main 6 inch sounds good to me.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 