ziptron
Materials
- Dec 9, 2010
- 64
Hi Everyone,
I am aware of a situation where an open to atmosphere Fire Water Storage Tank installed in a mechanical penthouse (not rooftop) of a building overflowed. It overflowed because a float switch failed to close. The overflow went into the mechanical room, flooded it and caused damage to the lower part of the building. The tank had no high level alarm so the owner had no clue that this was about to happen until it did.
I am now on a job site where I see a water storage tank in a similar configuration. Although it has a float switch, it has no high level alarm. I would love to convince the owner to install a high level alarm but I am getting push back. I think it should be done. Is anyone aware of codes/regulations that require high level alarms to be installed?
Drainage of overflow is not a good option as the building is old, tall and the current drain leader would not be able to carry away the entire amount of overflow (if it were to happen). Installing a leader big enough is just not possible.
I reviewed NFPA 22 and I am not seeing anything that specifically requires overflow warning/protection such as a high level alarm. I do see however in NFPA 25 that "How and Low level alarms should be tested semi-annually". I'm getting mixed signals here...
Any guidance would be appreciated, thanks!
I am aware of a situation where an open to atmosphere Fire Water Storage Tank installed in a mechanical penthouse (not rooftop) of a building overflowed. It overflowed because a float switch failed to close. The overflow went into the mechanical room, flooded it and caused damage to the lower part of the building. The tank had no high level alarm so the owner had no clue that this was about to happen until it did.
I am now on a job site where I see a water storage tank in a similar configuration. Although it has a float switch, it has no high level alarm. I would love to convince the owner to install a high level alarm but I am getting push back. I think it should be done. Is anyone aware of codes/regulations that require high level alarms to be installed?
Drainage of overflow is not a good option as the building is old, tall and the current drain leader would not be able to carry away the entire amount of overflow (if it were to happen). Installing a leader big enough is just not possible.
I reviewed NFPA 22 and I am not seeing anything that specifically requires overflow warning/protection such as a high level alarm. I do see however in NFPA 25 that "How and Low level alarms should be tested semi-annually". I'm getting mixed signals here...
Any guidance would be appreciated, thanks!