I'm referring to 'loose lintels' here, i.e. single angles that span over a window to support a single wythe of brick veneer and bear on the adjacent brick masonry at each end. My code states that these must be fireproofed for 'openings wider than 4 feet'. Any experience with this? It doesn't even say 'span more than 4 ft' in which case you could add intermediate hangers thereby reducing the span. Are people fireproofing loose lintels over a 5ft window? Particular case I'm looking at is metal stud backup to the brick veneer on a conc bldg. Code excerpt below:
704.11 Lintel protection:
Lintels over openings wider than 4 feet (1219 mm) in masonry walls, other than in walls of masonry veneer on wood frame structures, shall be fire protected as required by Section 704.3 when the full load over the opening is not relieved by a masonry arch of required strength.
Exceptions:1.The members of an assembled metal lintel that support only outer face masonry that is securely bonded or anchored to backing need not be fire protected, provided that the inner members of the assembly support the full load imposed.
704.11 Lintel protection:
Lintels over openings wider than 4 feet (1219 mm) in masonry walls, other than in walls of masonry veneer on wood frame structures, shall be fire protected as required by Section 704.3 when the full load over the opening is not relieved by a masonry arch of required strength.
Exceptions:1.The members of an assembled metal lintel that support only outer face masonry that is securely bonded or anchored to backing need not be fire protected, provided that the inner members of the assembly support the full load imposed.