FLA vs power consumption vs motor hp
mech4321
15
CA
We have to evaluate the power consumption at steady load of a fluid cooler which have at 600V an FLA of 23A. That would give approximately kw = 600 x 23 x 1.73 = 23.9 kw or 32 hp. However, the fluid cooler has only a total of motor of 6 x 1.5 hp = 9 hp (plus a small amount for the controls). Where does come this big differance? How can we evaluate the consumption if this value is not available from the manufacturer.
Alex
But there are only 6, not 9
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> faq731-376
Hit the Send button too quick.
It also does not say 23kVA, it says "23 FLA". So even if you are at 3A per 1-1/2HP 600V motor, that is still not getting to 23A.
My point is simply that the numbers do not add up in my opinion, so somewhere, there is data in/on that cooling system that is inaccurate or open to gross misinterpretation.
I think the quote sheet may list the wrong voltage.
Although for a slightly different product model number, the "-4B" specifies 460V motors with 115 volt controls. On that model the total watts is 8682 Watts (1447 W/Fan). The quote sheet also lists MCA/FLA/MOPD instead of FLA/MCA/MOPD. Would a power factor of 0.5 be reasonable. Assuming 0.5 pf gets you to the listed 21.6 FLA.
My bad on the number of motors, Jeff.
I was basing the KVA on this sentence from the first post.
"That would give approximately kw = 600 x 23 x 1.73 = 23.9 kw or 32 hp."
But I pretty much agree with you.
Time for us to stop guessing.
Bill
"Why not the best?"
Jimmy Carter