Boiler1
Mechanical
- Jun 3, 2004
- 40
Hi All,
I have got a curious situation where on a start-up the burner goes through the normal sequence ( i.e pilot flame followed by the staged flame ramp up) with no issues.
After about 15 min. the controller reads the ‘full flame’ or ‘full voltage’ (5V) from the flame rod . The furnace reaches the operating temperature in about 30min and from then on everything is stable for a while.
Anywhere between 15 and 24 hours into operation the voltage on the controller ( from the flame rod) drops down to 2-3 V while the furnace temperature remains unchanged (at the operation set point).
By now I have got the flame rod, the controller and the earth ( ground) wires replaced -to no avail. The only item in the loop that wasn’t changed is the flame rod power cable.
As mentioned the furnace temperature remains unchanged (fact) after the voltage drop and the flame as seen through the sight glass appears unchanged too – but that’s subjective.
Any ideas what the problem could be?
Kind regards
I have got a curious situation where on a start-up the burner goes through the normal sequence ( i.e pilot flame followed by the staged flame ramp up) with no issues.
After about 15 min. the controller reads the ‘full flame’ or ‘full voltage’ (5V) from the flame rod . The furnace reaches the operating temperature in about 30min and from then on everything is stable for a while.
Anywhere between 15 and 24 hours into operation the voltage on the controller ( from the flame rod) drops down to 2-3 V while the furnace temperature remains unchanged (at the operation set point).
By now I have got the flame rod, the controller and the earth ( ground) wires replaced -to no avail. The only item in the loop that wasn’t changed is the flame rod power cable.
As mentioned the furnace temperature remains unchanged (fact) after the voltage drop and the flame as seen through the sight glass appears unchanged too – but that’s subjective.
Any ideas what the problem could be?
Kind regards