WYSIWYG67
Mechanical
- Dec 9, 2021
- 13
I am working on evaluating pressure limits for an air system to be run at various temperatures in the creep range. This question concerns evaluating flange pressure limits according to ASME B16.5 (2009). I took a look at the pressure rating table for a 316ss flange at 1300°F (B16.5-Table II-2-2.2) and it doesn't jive with the pressure and temperature with which the facility was commissioned and has been running for decades.
316 is a Group 2 material and, per B16.5-NM Appendix A-2.3 the procedure states that for materials in the creep range (>950°F) that the allowable strength of BPVC Section II-D (2010) should be used. It also has notes about using 70% of yield strength at temperature, but yield strength isn't listed in the code beyond 1000°F.
So applying formula B16.5-2.1(eqn3)
Pt = C1*S1/8750*Pr ≤ Pc
C1=1
S1=4100 psi (@ 1300°F)
Pr=flange class=1500
Pc=ceiling pressure per B16.5-Table A-2= 685 psi
Pt=702.9 psi which is not less than 685 psi, so the flange should be rated to 685 psi. However, Table II-2-2.2 (2009) shows that at 1300°F the flange has a listed pressure rating of 585 psi. Our facility has been around since the 1960's an the guys who designed it were pretty smart fellas, so I know they would not have made such a basic mistake.
My main question is why doesn't B16.5-2.1(eqn3) come up with the same rating as B16.5-Table II-2-2.2? In B16.5 it states that "Pressure–temperature ratings for this Standard have been determined by the procedures described in this Nonmandatory Appendix."
This is puzzling me and our operations engineers. Thanks for any input.
316 is a Group 2 material and, per B16.5-NM Appendix A-2.3 the procedure states that for materials in the creep range (>950°F) that the allowable strength of BPVC Section II-D (2010) should be used. It also has notes about using 70% of yield strength at temperature, but yield strength isn't listed in the code beyond 1000°F.
So applying formula B16.5-2.1(eqn3)
Pt = C1*S1/8750*Pr ≤ Pc
C1=1
S1=4100 psi (@ 1300°F)
Pr=flange class=1500
Pc=ceiling pressure per B16.5-Table A-2= 685 psi
Pt=702.9 psi which is not less than 685 psi, so the flange should be rated to 685 psi. However, Table II-2-2.2 (2009) shows that at 1300°F the flange has a listed pressure rating of 585 psi. Our facility has been around since the 1960's an the guys who designed it were pretty smart fellas, so I know they would not have made such a basic mistake.
My main question is why doesn't B16.5-2.1(eqn3) come up with the same rating as B16.5-Table II-2-2.2? In B16.5 it states that "Pressure–temperature ratings for this Standard have been determined by the procedures described in this Nonmandatory Appendix."
This is puzzling me and our operations engineers. Thanks for any input.