We have a shell and tube heat exchanger (cooling water on tube side) located above a condensate receiver. It is used to condense flash steam from the receiver & return it back to the receiver. The cooling water flow through the condenser is controlled to maintain receiver pressure at 30 psig. Also there is level control on the receiver. Both pressure & level control seem to be fine. The steam/condensate mixture comes to the tank from 2 therm rolls on our papermachine calendar stack. The steam is fed to the shell of each therm roll (longitudinal holes drilled through shell) & the exiting condesate/ steam mixture is returned to the receiver located in the basment approx. 30' below the calendar. There is a bleed line off the top of the vent condenser which runs to a floor drain. We have to keep this bleed open all the time or else there is constant hammering inside th condenser. Even with this drain open there is still a lot of hammer but not as loud. The condenser is located approx 3' above the receiver & the "steam supply" & "condensate return" lines between the top of the receiver & the bottom of the condenser are the same diameter & approx. the same length. Any thoughts as to how to stop the hammer? We recently had to sewer the condensate tank as there is cooling water passing into the receiver due to leaks in tubes.