Don't do it. You have a 1/8" per foot slope- water will tavel slowly down it. If you use aluminum flashing over your membranes, it will be mechanically attached. You will have many penetrations through your aluminum flashing "shingles" and slow moving water. This translates into leaks. Even if you use gasketed fasteners, your "shingle" material is not self-healing (as are membrane roofing and shingles, to a degree) or compressible enough to allow a watertight fit (as are single-ply systems made for mechanical attachment).
Even caulking the hell out of all your penetrations with a good sealant isn't the answer- 1) you will create all sorts of nooks and crannies to catch and hold water which will- believe me- eventually find a way in or freeze and force openings, and 2) even a "20 year" sealant won't work more than 10 years in this environment, with long-term exposure to water and an elastomeric surface (ice and water shield) as one of its substrates.
Similarly, adhesive or caulk attachment of the aluminum, in lieu of mechanical attachment, will fail. In this case however, a good ice and water shield over the entire roof may save you (if the adhesive doesn't eat it). It may act as a roof on its own.
With your slope, membrane roofing of some sort is required. Remember, even for the best standing seam metal roofs, 1.5" per foot is the minimum slope, and for the best shingle roofs, 2.5" per foot is the minimum slope. For less slope than that, you need a continuous membrane to keep the water out.
I would recommend modified bit roofing for your project, torch applied or hot-mopped. Follow the manufacturer's instructions, put down a recovery board over the deck (you'll be less likely to damage the membrane during installation and when walking on the roof), a base sheet, and the your modified bit (much thicker and more ductile than tar and felt). As an alternate, believe it or not, a 3-, 4-, or 5- ply tar and felt roof is still a good long-term solution to a low-slope roof such as yours.
Because of cost and the size of your project, some of the better commercial-grade membrane systems are not appropriate for your project, but there are some great systems out there these days.
Of course flashing is key. Do it right.
By the way, I'm a licensed architect as well as a structural guy, so I know a bit about roofing. I design roofing systems all the time.