VT17
Structural
- Apr 27, 2018
- 14
Hello all,
I've been searching on this forum and online as to how to design flexible roof diaphragms in a steel building but there are some things I'm still not clear about which I would really appreciate your input on.
Please see the attached document that has a roof plan and which I'm using as a reference for my below questions. For simplification purposes, let's assume all factors (LRFD or ASD) are 1.0 when selecting an appropriate diaphragm and each question is unrelated to the next unless stated otherwise.
1) When analyzing at the interior frame (BF2) to size the diaphragm for w1, does the shear strength of the diaphragm have to be greater than 50k/150ft or 100k/150ft? If you say it's 50k/150ft would the attachment pattern along this beam line only have to be double (i.e. if a 36/7 pattern works, would the pattern along this beam line have to be 36/14)?
2) How do you actually determine the shear demand on the diaphragm? For instance, when sizing the diaphragm for w2, would you consider the shear demand to be 100k/200ft and then also design the 3 other beams (in red at the bottom) as collector elements? Or could you say its 100k/100ft and only design one beam as a chord element (like shown in red at the top)
3) Assume that when designing for w1 (ignore the loads provided in that direction) you choose a diaphragm that has the capacity of 2klf. When checking if it works for the w2 load stated, it's obvious the deck can transfer all 100kips to BF4 (or BF5) across the length of the brace frame only. In that case, (ignoring the potential rollover capacity of the joists), is there a need to design any of the adjacent beams as collector elements?
4) Related to question 3. Even if there's no need to design the other beams as collector elements, wouldn't the lateral load on the joist seats at BF4 then be 100k/10 = 10k which would far exceed its rollover capacity? If you were adamant about your connection detail in this direction to not include an hss (or similar) member between each joist to prevent rollover of the joist seats, wouldn't you then have to design all 3 of the beams along that line as collector elements so that the lateral load per joist seat would then be 100k/40 = 2.5k which is around the rollover capacity?
My apologies if this is a lot. I think I've honestly put good effort into trying to figure this out but I either can't find a source that explains the above or when I think I have made sense out of it, I double guess myself and as a recent grad, I do not want to improperly design this aspect of a building. Thank you everyone in advance!
I've been searching on this forum and online as to how to design flexible roof diaphragms in a steel building but there are some things I'm still not clear about which I would really appreciate your input on.
Please see the attached document that has a roof plan and which I'm using as a reference for my below questions. For simplification purposes, let's assume all factors (LRFD or ASD) are 1.0 when selecting an appropriate diaphragm and each question is unrelated to the next unless stated otherwise.
1) When analyzing at the interior frame (BF2) to size the diaphragm for w1, does the shear strength of the diaphragm have to be greater than 50k/150ft or 100k/150ft? If you say it's 50k/150ft would the attachment pattern along this beam line only have to be double (i.e. if a 36/7 pattern works, would the pattern along this beam line have to be 36/14)?
2) How do you actually determine the shear demand on the diaphragm? For instance, when sizing the diaphragm for w2, would you consider the shear demand to be 100k/200ft and then also design the 3 other beams (in red at the bottom) as collector elements? Or could you say its 100k/100ft and only design one beam as a chord element (like shown in red at the top)
3) Assume that when designing for w1 (ignore the loads provided in that direction) you choose a diaphragm that has the capacity of 2klf. When checking if it works for the w2 load stated, it's obvious the deck can transfer all 100kips to BF4 (or BF5) across the length of the brace frame only. In that case, (ignoring the potential rollover capacity of the joists), is there a need to design any of the adjacent beams as collector elements?
4) Related to question 3. Even if there's no need to design the other beams as collector elements, wouldn't the lateral load on the joist seats at BF4 then be 100k/10 = 10k which would far exceed its rollover capacity? If you were adamant about your connection detail in this direction to not include an hss (or similar) member between each joist to prevent rollover of the joist seats, wouldn't you then have to design all 3 of the beams along that line as collector elements so that the lateral load per joist seat would then be 100k/40 = 2.5k which is around the rollover capacity?
My apologies if this is a lot. I think I've honestly put good effort into trying to figure this out but I either can't find a source that explains the above or when I think I have made sense out of it, I double guess myself and as a recent grad, I do not want to improperly design this aspect of a building. Thank you everyone in advance!