I've got a 'beam' section that is 22" wide by 118" deep and 114" long. Factored moment on the beam is 188.61 kip-ft so I'm getting from analysis .32 in2 of steel required. The minimum steel from ACI 318 comes to 8.45in2. Is this where section 9.6.1.3 comes into play? Saying that if As is 1/3 above As required by analysis then you don't need to follow 9.6.1.2 and 9.6.1.1?
Just seems wild to me that the code calls for over 8in2 of reinforcement but only need .44in2. I just wanted to make sure I'm understanding the code correctly.
Just seems wild to me that the code calls for over 8in2 of reinforcement but only need .44in2. I just wanted to make sure I'm understanding the code correctly.