robsalv
Mechanical
- Aug 8, 2002
- 311
In Australia, when a boiler has been down for an inspection or overhaul, or for a safety relief valve overhaul, it's standard practice to do a controlled lift of the safety valve [boiler firing against the blocked stop valve with superheater vents open to keep some flow]. We record lift and reseat pressures. We try not to lift and or adjust the SV settings more than 3 times, otherwise the SV will leak on line.
There is a move by occupational health and safety folk to stop this practice because of the noise involved. In my experience, trevi testing is not a total answer - so I'm on the side of floating SV's.
Is this "floating" a common Australian practice? If not, has anyone gone from floating to not floating when recommissioning their boilers?
Thanks
Rob