Floating System/UPS

Status
Not open for further replies.

Seamus59

Electrical
Aug 19, 2003
1
We are currently on an offshore production unit and we have a concern that the UPS transformer secondary has not got the neutral line bonded to earth.
Primary is 415 Volts 3 phase and Secondary is 240 volts 1 phase.
 
Replies continue below

Recommended for you

This appears to be common among some UPS systems. Check with the manufacturer and see if it is required. Otherwise, check with the code for your location.
 
Suggestion: The grounded neutral to the platform shall result in approximately 240V between each phase and the platform ground. If the voltage is less, then there will not be a good connection between the UPS transformer secondary and the platform ground. E.g. 200W bulb connected between a phase and ground might reveal the neutral grounding status.
 
You should bond/earth the N on the tranf second forthwith.
 
Ground it to the platform steel [or if you have a common ground, there] and that will take care of your problem.

 