I have a case where I have the head of window mullions that is set on the foundation wall butting into the underside of some framing that is supported by the roof structure. Therefore, the window will not be moving up or down, but the framing above it will be. The window suppilier will need to aacomadate the movement of the roof structure with his system.
On the drawings the window suppilier was told to design his windows system for 1/2" vertical movement in the structure above
Now that he has the job, he is wining that 1/2" live load deflection is " very large" and that they " typically see 1/4" live load deflections ".
I have never seen, or designed to such a tight criteria. The some of the roof beams are 54 feet long, so the 1/2" live load deflection limit is already L/1,296. This seem very reasonable to me.
I would like to know what kind of live load deflections limits others typical show for window suppiliers to design too, and if you think a 1/2" limit is unreasonably large.
Thank You.