I have a question about construction of floor slabs and whether or not a much lower strength than specified would be an issue to other structural engineers. I have a project that has a small elevated slab as well as some of the slab on grade that came back with f'c test results of around 2200 psi.
My drawings spec'd 4000 psi concrete and all of the rest of the concrete on the project has been fine. Apparently, the concrete that did come back negative was a different mix design than the rest of the concrete for the project to enable them to pump it through a 2" line. It is a 4000 psi mix that the ready mix plant has used in the past with success.
After the 28 day results came back so poorly (2200 psi average), we had them take some cores and saw as bad as 1450 psi on the worst core and as good as 2300psi in the best case. The contractor is obviously trying to avoid tear out and replacement since it will back up their schedule but I don't know if I have much of a choice other than to have them tear it out.
Now they went ahead and did an ASTM C803 Winston probe test and are seeing results of 3600psi or greater. While this test yields better results, I'm hesitant to accept it to be the same as the cylinder tests.
Any feedback would be great. Is the biggest concern durability for a slab? What would you do as the engineer?
My drawings spec'd 4000 psi concrete and all of the rest of the concrete on the project has been fine. Apparently, the concrete that did come back negative was a different mix design than the rest of the concrete for the project to enable them to pump it through a 2" line. It is a 4000 psi mix that the ready mix plant has used in the past with success.
After the 28 day results came back so poorly (2200 psi average), we had them take some cores and saw as bad as 1450 psi on the worst core and as good as 2300psi in the best case. The contractor is obviously trying to avoid tear out and replacement since it will back up their schedule but I don't know if I have much of a choice other than to have them tear it out.
Now they went ahead and did an ASTM C803 Winston probe test and are seeing results of 3600psi or greater. While this test yields better results, I'm hesitant to accept it to be the same as the cylinder tests.
Any feedback would be great. Is the biggest concern durability for a slab? What would you do as the engineer?