Floor Slab Thickness Design Using PCA Charts for Rack Storage Post Loading 2

Status
Not open for further replies.

jheidt2543

Civil/Environmental
Sep 23, 2001
1,469
I have a floor slab to design to support storage rack W6 posts with a 14 kip load. The PCA Charts do not have a wide enough range for the X and Y distances between posts to cover my situation (X = short distance = 138" and Y = long distance = 240"). I'm wondering what others do when they run into this situation; look at each post as an individual load, analyse it as a beam on an elastic foundation, other?
 
Replies continue below

Recommended for you

jheidt2543...shear will probably control unless your post spacing is quite close. With your spacing, the slab will not likely act like a beam, but will have an isolated punching load.