Giorgos Papakonstantinou
Mechanical
- Apr 7, 2020
- 1
I am confused in selecting the correct pump for a fire fighting system which has automatic sprinklers and fire hoses.
So in a building where there is already an installed combined system with fire hoses and sprinklers, there is a pump which supplies both, through a manifold with two risers (one for the fire hoses and one for the sprinklers). On this system I am asked to check whether the pump installed, is correct to supply both systems the required pressure and water flow.
I model this scenario in EPANET by choosing the most unfavorable set of 12 sprinklers and the most unfavorable fire hose working simultaneously (each sprinkler with an emitter coefficient and no base demand, and the fire hose with a base demand 380 l/min).
Now I should select a pump which provides at least 4.4bar at the fire hose, and at least 60 l/min and 0.563 bar (5.74 m) at the most distant sprinkler from the set of 12.
Solving the above scenario in EPANET with a certain pump provides the minimum requirements for the sprinklers, but does not satisfy the minimum pressure demand for the fire hose.
Solving the same scenario in EPANET with a bigger pump, satisfies the minimum pressure demand for the fire hose, but it increases substantially the pressure and flow at the sprinklers.
So I doubt myself whether is a good strategy to simulate both sprinkler and fire hose simultaneously.
I have attached my model in EPANET (it uses SI units). If you see I get 47m pressure and 380 l/min but the last sprinkler has double the required pressure and 1.5 the flow (13m pressure and 91 l/min).
What are you suggestions and opinion? Thank you in advance
So in a building where there is already an installed combined system with fire hoses and sprinklers, there is a pump which supplies both, through a manifold with two risers (one for the fire hoses and one for the sprinklers). On this system I am asked to check whether the pump installed, is correct to supply both systems the required pressure and water flow.
I model this scenario in EPANET by choosing the most unfavorable set of 12 sprinklers and the most unfavorable fire hose working simultaneously (each sprinkler with an emitter coefficient and no base demand, and the fire hose with a base demand 380 l/min).
Now I should select a pump which provides at least 4.4bar at the fire hose, and at least 60 l/min and 0.563 bar (5.74 m) at the most distant sprinkler from the set of 12.
Solving the above scenario in EPANET with a certain pump provides the minimum requirements for the sprinklers, but does not satisfy the minimum pressure demand for the fire hose.
Solving the same scenario in EPANET with a bigger pump, satisfies the minimum pressure demand for the fire hose, but it increases substantially the pressure and flow at the sprinklers.
So I doubt myself whether is a good strategy to simulate both sprinkler and fire hose simultaneously.
I have attached my model in EPANET (it uses SI units). If you see I get 47m pressure and 380 l/min but the last sprinkler has double the required pressure and 1.5 the flow (13m pressure and 91 l/min).
What are you suggestions and opinion? Thank you in advance