Flue gas question 1
kbs
126
Is there a formula that would give me the volume of flue products leaving a boiler if I know the btu/hr, temp. of flue gases, percent O2, CO2 and excess air. I am trying to size an economizer for a small boiler (4100cf/hr CH4) and use the captured heat to help heat a swimming pool.
In the past, I have measured velocity of flue gases and, using velocity and volume formulas, found the volume of gases that way. Just curious if there is another way.
Thanks for any help.
kbs:
Using a pitot tube to ascertain the flue gas velocity and then calculating the volumetric flow rate of the flue gas is a good way of doing what you want.
If you could contact a chemical engineer and ask him/her to perform a combustion calculation to obtain the volumetric flow is another way of doing it. Assuming that you are talking about a natural gas fuel, a "ball-park" figure is 11,000 to 12,000 standard cubic feet of wet flue gas per million Btu of fuel gas. (Standard cubic feet are measured or calculated at 60 degrees F and atmospheric pressure).
Milton Beychok
(Contact me at www.air-dispersion.com)
Thanks for the input. Stoichemetric combustion would be approximately 10 to 1 but how would the excess air percentage be worked out. Would 50% excess air be the equivalent of 5 times the cu.ft of gas? Oh, yes it is natural gas at 1040 btu/cuft.
Thanks again for the help.
kbs:
Going through the detail of a combustion calculation by posting a message on an online forum is just too difficult and time consuming. Any chemical engineer you contact can and should be able to easily work such a calculation through for your boiler's specific amount of excess combustion air (which is not the same as the amount of oxygen in your flue gas).
I very seriously doubt that your boiler uses 50 percent excess combustion air ... it probably uses 5 to 10 percent excess combustion air or even less.
The number that I gave you in my earlier response (11,000 to 12,000 standard cubic feet of wet flue gas per million Btu of fuel gas) was based on a combustion calculation using a natural gas with a heating value of 1093 Btu/scf and 12 percent excess combustion air.
Milton Beychok
Hi Milton
As an industrial gasfitter I regularly use combustion analyzers. My current is a KaneMay Equinox. It measures excess air in percentages above stoichemetric. On the smaller (under 400hp) package non-condensing hot water boilers such as Cleaver Brooks, their design rarely allows less than 20% excess air. My example of 50% was used in context.
I can always tell how much natural gas is entering the combustion chamber using manifold pressures, and have always measured flue gas volumes using a pitot tube and with velocity and volume formulas. I was hoping there may be a rule of thumb method I could use from the analyzer printouts to get a flue gas volume instead of climbing and drilling into stacks.
The rule of thumb we use is 10 cuft air to 1 cuft gas for near stoichemetric. Therefore 10% excess would be 1 extra cuft of air than is required. This acheives what you find with your calc.
All in all, I think you are right, measuring the velocity, etc. is probably my best alternative.
Thanks for your input.
kbs
kbs:
Let's do it quick and dirty by assuming that natural gas is pure methane (actually, most natural gas is 90 to 95% methane). Now let's write the equation for the combustion of methane (CH4) at exactly stoichiometric conditions (which means no excess combustion air):
CH4 + 2 02 + 8 N2 ==> CO2 + 2 H2O + 8 N2
In English, the above equations says that 1 mole of methane plus 10 moles of air (i.e., 2 moles of oxygen plus 8 moles of nitrogen) will burn to yield 11 mols of wet flue gas (i.e., 1 mole of carbon dioxide plus 2 moles of water vapor plus 8 moles of nitrogen).
Since moles are directly proportional to standard cubic feet (scf) of any gas, we can say that:
Burning 1 scf of natural gas requires at least 10 scf of air ... which is your rule of thumb
and also:
1 scf of natural gas burns to yield 11 scf of wet flue gas
and since 1 scf of natural is about 1,000 Btu, we can also say that:
1,000 btu of natural gas burns to yield 11 scf of wet flue gas
Therefore:
1,000,000 Btu of natural gas burns at stoichiometric conditions to yield 11,000 scf of wet flue gas which is pretty darn close to the ball-park figure I gave you for burning fuel gas with 10 percent excess combustion air.
Milton Beychok
Hi Milton, I can work with this. Thanks for your patience and info.
