Flushing connection requirement

Status
Not open for further replies.

JigarJoshi

Electrical
Dec 20, 2015
11
Can anyone tell me that Why and for which Process condition Flushing connections required(For Diaphragm Seal Transmitters)??
 
Replies continue below

Recommended for you

Sludge or precipitating deposits that can block pressure transfer to the diaphragm need to be removed by flushing.

For instance, Lime slurry will deposit both lime and impurities that over time will block the slurry's hydrostatic pressure from contacting the sensing diaphragm.
 