SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,244
The building in question is existing and your standard rigid frame and 8" bent metal purlin building that is exactly 35'-0" tall at the peak having a 1" in 12" pitch.
Unlike all other rigid frame buildings this one has 24'-0" bays. This is so unusual that tomorrow I am driving 220 just north of Atlanta to double check the bay spacing just to make double sure they are all 24' bays.
Rack storage and the FM rep told me to use Table 8 found in 8.9.
I would like to use the Tyco K25.2EC upright sprinklers and it appears to me that 8 sprinklers discharging at 40 psi would be an acceptable alternative design.
It appears, and I can certainly be wrong here, that Reliable is the only one that manufactures and FM approved EC25.2 pendent? With the maximum spacing of 12' between heads you can understand why it is so important for me to verify that we do have all bays at 24' and that a 25' bay isn't hidden in on me somewhere.
And I believe the maximum size of line I can have is 2 1/2" for the upright K25.2EC. I don't think anything larger than 2 1/2" can be used on an upright sprinkler unless it is on a sprig up that would be massive.
And for some reason I believe it is calculating four open sprinklers on two branch lines?
The water supply could certainly be better but hat we have is a 1,500 gpm 50 psi booster pump taking suction from a city water main. What I have to work with is 110 psi at churn, 84 psi @ 1,500, 71 psi @ 1,700, 63 psi @ 1,800 and 59 psi @ 1,900. I wish it was a 100 psi booster and not a 50 psi but that is what I have to work with so you can see the sprinklers I have to work with is rather limited. Reality tells me it is going to be the K25.2 EC or the K22.4.
So, am I reading the table correctly that I can use a Tyco K25.2EC UPRIGHT discharging 8 sprinklers at 40 psi with 250 gpm hose? That I would be discharging 4 sprinklers from two lines?
I know this is just a forum but I want everyone to rest assured I will certainly talk to the FM representative before I do anything (like give a price) just to make sure it is all clear in my head.
Unlike all other rigid frame buildings this one has 24'-0" bays. This is so unusual that tomorrow I am driving 220 just north of Atlanta to double check the bay spacing just to make double sure they are all 24' bays.
Rack storage and the FM rep told me to use Table 8 found in 8.9.
I would like to use the Tyco K25.2EC upright sprinklers and it appears to me that 8 sprinklers discharging at 40 psi would be an acceptable alternative design.
It appears, and I can certainly be wrong here, that Reliable is the only one that manufactures and FM approved EC25.2 pendent? With the maximum spacing of 12' between heads you can understand why it is so important for me to verify that we do have all bays at 24' and that a 25' bay isn't hidden in on me somewhere.
And I believe the maximum size of line I can have is 2 1/2" for the upright K25.2EC. I don't think anything larger than 2 1/2" can be used on an upright sprinkler unless it is on a sprig up that would be massive.
And for some reason I believe it is calculating four open sprinklers on two branch lines?
The water supply could certainly be better but hat we have is a 1,500 gpm 50 psi booster pump taking suction from a city water main. What I have to work with is 110 psi at churn, 84 psi @ 1,500, 71 psi @ 1,700, 63 psi @ 1,800 and 59 psi @ 1,900. I wish it was a 100 psi booster and not a 50 psi but that is what I have to work with so you can see the sprinklers I have to work with is rather limited. Reality tells me it is going to be the K25.2 EC or the K22.4.
So, am I reading the table correctly that I can use a Tyco K25.2EC UPRIGHT discharging 8 sprinklers at 40 psi with 250 gpm hose? That I would be discharging 4 sprinklers from two lines?
I know this is just a forum but I want everyone to rest assured I will certainly talk to the FM representative before I do anything (like give a price) just to make sure it is all clear in my head.